This topic provides an overview of how to configure network connections to support Equinix Precision Time subnets. Your equipment connects to Precision Time through Equinix Fabric.

NTP network model with a single customer subnet connected through Equinix Fabric to two Precision Time masters

The following topology discussions show how to configure your network, depending on whether you're using Network Time Protocol (NTP) or Precision Time Protocol (PTP).

Time Server 1 in one Equinix Precision Time service location is not the same host as Time Server 1 in another service location. Each location uses separate, geographically distinct time servers, providing true geo‑redundancy.

Network Configuration for Equinix Precision Time and NTP​

Your network configuration depends on the number of NTP subnets in your network. The options are to configure either a single subnet or multiple subnets.

Configuring NTP with a Single-Subnet Network​

These examples show non-redundant network configurations for an NTP service with a single subnet on your side.

For a non-redundant configuration:

NTP network model with a single customer subnet connected through Equinix Fabric to two Precision Time masters

note

In this example, if you use subnet 192.168.1.0/24, you can use any IP for your end device within that subnet, excluding IP addresses 192.168.1.21/24 and 192.168.1.22/24 (the two IP addresses set on the time servers).

  1. Configure the end device that needs to be synchronized with an IP address that is within the same subnet range as the one configured for the time servers on the Equinix Customer portal.

  2. Ping the time server IP (here, either 192.168.1.21 or 192.168.1.22). The response should show the time server is under the same subnet that is configured for the interface of your end device (in this example, 192.168.1.0/24). Continue configuring your NTP client only if you get a successful Ping response.

  3. Configure both time server IP addresses (192.168.1.21 and 192.168.1.22 in this example) in the server section of the NTP client configuration file.

  4. Start your NTP client.

Configuring NTP with a Multiple-Subnet Network​

These examples show non-redundant network configurations for an NTP service with multiple subnets on your side.

For a non-redundant configuration:

NTP network model with multiple customer subnets connected through Equinix Fabric

info

When using NTP, Equinix Precision Time supports multiple subnets with only the Enterprise service tier; Precision Time does not support multiple subnets with NTP at the Standard service tier level.

  1. Provide Equinix with the configuration information for your gateway interface so that we can provision a new service connection in Equinix Customer portal.

    • The gateway interface must be within the subnet directly connected to the Equinix Precision Time service.
    • The gateway interface must be interconnected with other subnets.
  2. Configure the end device that needs to be synchronized with an IP address that is within the same subnet range as one of your configured subnets.

  3. Ping the time server IP (for example: 192.168.1.21 or 192.168.1.22). Continue to configure your NTP client only if you get a successful Ping response.

  4. Configure both time server IP addresses (here, 192.168.1.21 and 192.168.1.22) in the server section of the NTP client configuration file.

  5. Start your NTP client.

Network Configuration for Equinix Precision Time and PTP​

PTP requires hardware timestamping on network interfaces and network devices. Your network configuration depends on the number of PTP subnets in your network: single or multiple.

PTP Domain Configuration​

The PTP domain number is configurable in the Advanced PTP Configuration settings in the Customer portal. New connections default to domain 0. Previously, the default domain was set to 30.

Configuring PTP with a Single-Subnet Network​

These examples show non-redundant network configurations for a PTP service with a single subnet on your side.

For a non-redundant configuration:

PTP network model with a single customer subnet connected through Equinix Fabric

  1. Ensure all devices in the integration have network interface cards that support hardware timestamping.

  2. Run ethtool -T <interface_name> to ensure the network interface supports IEEE 1588 PTP and the necessary hardware timestamping options.

  3. Configure the end device that needs to be synchronized with an IP address that is within the same subnet range as the one configured for the time servers on Equinix Customer portal. In this example, if you use subnet 192.168.1.0/24, you can use any IP for your end device within that subnet, excluding IP addresses 192.168.1.21/24 and 192.168.1.22/24 (the two IP addresses set on the time servers).

  4. Ping the time server IP (here, either 192.168.1.21 or 192.168.1.22). The response should show the time server is under the same subnet that is configured for the interface of your end device (192.168.1.0/24 in above diagram).

  5. If you get a successful Ping response, you may start your PTP client in multicast mode.

note

Because the client operates in multicast mode, a primary clock IP does not need to be specified. The client automatically discovers the time source within the subnet.

Configuring PTP with a Multiple-Subnet Network​

These examples show non-redundant network configurations for a PTP service with multiple subnets on your side.

For a non-redundant configuration:

PTP network model with multiple customer subnets connected through Equinix Fabric

  1. Provide Equinix with the configuration information for your gateway interface so we can provision a new service connection in Equinix Customer portal.

    • The gateway interface must be within the subnet directly connected to the Precision Time service.
    • The gateway interface must be interconnected with other subnets.
  2. If more than one routing device is configured between subnets, you need to configure the gateway interface routing device and other routing devices.

    • Preferably, these should be hardware devices with PTP support.
    • The routing devices must support multicast routing, specifically the PIM and IGMP protocols.
  3. The PIM and IGMP protocols must be configured on all routing devices operated between subnets.

  4. Ensure all network interface cards provide hardware timestamping support.

  5. Run ethtool -T <interface_name> to ensure the network interface supports IEEE 1588 PTP and the necessary hardware timestamping options.

  6. Configure the end device that needs to be synchronized with an IP address that is within the same subnet range as one of your configured subnets.

  7. Ping the time server IP (here, either 192.168.1.21 or 192.168.1.22). The response should show the time server is under the same subnet that is configured for the interface of your end device.

  8. If you get a successful Ping response, you can start your PTP client in multicast mode.

note

In multicast mode, a primary clock IP does not need to be specified. The client automatically detects the time source when both the client and time server are within the same subnet.